I'm using Trend control. I want to enter 10 different values:
1. Name(Temp1) > Style > Trend values (100) > Trend type (Cyclical real time) > Source settings (1 st tag from PLC) and so on , however I'm not able to add more than 4 data source.
Is there any limitation? Or I have to do some settings.
Thank you.
Regards,
Erick
Unfortunately, the trend control for the KTP-series of HMI panels is limited to 4 data sources. It is possible to add multiple trend controls to the same screen.